Mod. BRCQ0481BD Help please

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
allen655
Posts: 4
Joined: Thu Jun 10, 2010 8:22 am

Please help. Have mod brcq0481bd condensing unit that will not start.
Have power through the contactor, and you can hear the compressor kind of growl but will not start and no fan.
Could this be the start capacitor gone bad. Note two days before the problem started something tripped the main breaker
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

May be a bad dual run capacitor, see if it is leaking or swollen any or bulging.

Dual Run Capacitor # G32-476 can be seen and ordered here if needed:

http://www.aberdeenhomerepair.com/store ... 7%7D5-440V


This may or may not resolve the issue, would take testing of circuit and components to know for sure.


IF full 240vac is getting through the contactor and neither compressor or condenser fan is running, it is a possibility of a bad run capacitor.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
allen655
Posts: 4
Joined: Thu Jun 10, 2010 8:22 am

Robert, tahnks that fixed the problem.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

You're very welcome, happy to help.



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?