Hi there -
Found my heat was coming on, but it did not want to stay on, and reach desired temperature. After playing with it, and turning Fan onto ON (instead of Auto) position, the fan would not run. If I jacked up the temp or lowered it on the thermostat, all I got was clicks. After it sits for a bit, the fan will start blowing again.
Had amperage checked, and it seems to be drawing a wee over 6 AMPS vs the 4AMPS it should. Thinking, bad relay or bad motor? It sounds as if its having a hard time getting enough airflow, almost(?)
If it is the motor is Blower Motor # 1468-243P/A the correct one?
And what does usual labor this would run?
Thanks in advance
EB17B - BLOWER SEEMS to be Overheating?
Could also be a bad run capacitor. When you checked the amps, did you have the door off ?
Labor varies from company to company, just depends.
Blower Motor # 1468 - 243P/A is correct. Would need a new run capacitor if you replaced the motor.
I would look closely at the fan relay, sequencer and run capacitor first.
Sequencer controls motor during heat cycle, but it goes through the fan relay.
Fan relay controls it during cooling cycle.
Thanks,
Robert
Labor varies from company to company, just depends.
Blower Motor # 1468 - 243P/A is correct. Would need a new run capacitor if you replaced the motor.
I would look closely at the fan relay, sequencer and run capacitor first.
Sequencer controls motor during heat cycle, but it goes through the fan relay.
Fan relay controls it during cooling cycle.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Help! Possible no tie downs, home seems quite unstable
by Theflyinggiraffe » Sun Jun 09, 2019 10:00 am » in Mobile Home Repair - 2 Replies
- 3342 Views
-
Last post by Mark440
Tue Jun 11, 2019 11:04 pm
-
-
- 2 Replies
- 60298 Views
-
Last post by jazsimpson
Sat Jul 08, 2017 8:16 am
-
-
Need advice on blower
by NorthTexasSafariGuy » Mon Jul 31, 2017 9:18 am » in Coleman Service & Repair - 0 Replies
- 70624 Views
-
Last post by NorthTexasSafariGuy
Mon Jul 31, 2017 9:18 am
-
-
-
Blower fan acting up 7995-656/d
by Michael Yep » Fri Oct 06, 2017 11:26 am » in Coleman Service & Repair - 0 Replies
- 36437 Views
-
Last post by Michael Yep
Fri Oct 06, 2017 11:26 am
-
-
- 0 Replies
- 57573 Views
-
Last post by Montanan
Wed Jan 03, 2018 1:03 pm