Posted: Fri Nov 19, 2010 6:59 pm
Hi,
I am working on a Pres II model 7663B 856 series. When the thermostate is engaged the burner comes on and the unit heats up, the blower comes on and runs for about a minute and then shuts off. The burner remains on. After a while about 6 minutes the blower comes on a runs for a minute and then shuts off. Called a service man, he thought my valve was bad because the burner flame did not appear as intense as it should have. He replaced the valve, no change in flame or blower motor operation.
I read through your forums and discovered that the diagnosis was that my fan/limit switch was bad or I could possibly have an air leak causing the sensor to cool off and turn the blower off. I replaced the fan/limit switch. The blower will run for about 3 to 4 minutes now but then cycle off. I went ahead and replaced the lower limit switch. No change.
I am not sure what to check next. The thermostate reads 25 volts. The thermostate lines to the valve read 25 volts when thermostat is engaged and 0 volts when not. When the blower is not running the fan/limit switch is reading 120 from point to point and 0 when running. I can not get any readings from the lower limit switch from point to point whether running or not. I get 120 when I test each individual point to ground (heater cabinet). I can jumper the fan/limit switch and the blower will run until I remove the jumper.
Could it be that my burner flame is not high enough or hot enough? How can I test to see if cold air is comming from somewhere and cooling the sensors down? Is there a way to adjust the flame of the burner? I am confused and lost. Heelllppp
I am working on a Pres II model 7663B 856 series. When the thermostate is engaged the burner comes on and the unit heats up, the blower comes on and runs for about a minute and then shuts off. The burner remains on. After a while about 6 minutes the blower comes on a runs for a minute and then shuts off. Called a service man, he thought my valve was bad because the burner flame did not appear as intense as it should have. He replaced the valve, no change in flame or blower motor operation.
I read through your forums and discovered that the diagnosis was that my fan/limit switch was bad or I could possibly have an air leak causing the sensor to cool off and turn the blower off. I replaced the fan/limit switch. The blower will run for about 3 to 4 minutes now but then cycle off. I went ahead and replaced the lower limit switch. No change.
I am not sure what to check next. The thermostate reads 25 volts. The thermostate lines to the valve read 25 volts when thermostat is engaged and 0 volts when not. When the blower is not running the fan/limit switch is reading 120 from point to point and 0 when running. I can not get any readings from the lower limit switch from point to point whether running or not. I get 120 when I test each individual point to ground (heater cabinet). I can jumper the fan/limit switch and the blower will run until I remove the jumper.
Could it be that my burner flame is not high enough or hot enough? How can I test to see if cold air is comming from somewhere and cooling the sensors down? Is there a way to adjust the flame of the burner? I am confused and lost. Heelllppp