Page 1 of 1
Nordyne FEH-105HA-04
Posted: Sat Dec 04, 2010 12:34 pm
by Cindy_R
I have a heat/AC furnace in my mobile home. The heat was not working so the service man changed the relay switch and the thermostat. It worked for a few hours and hasn't since. My air was working before he changed the thermostat. My question is does this sound like a blower motor problem? Any input would be appreciated. Thanks
Re: Nordyne FEH-105HA-04
Posted: Sun Dec 05, 2010 3:09 am
by Robert
No heat at all ? Lower heat temp than normal ? No blower motor ?
One of these or all ?
Sequencer controls elements and blower motor.
Thanks,
Robert
Re: Nordyne FEH-105HA-04
Posted: Sun Dec 05, 2010 11:26 am
by Cindy_R
Before the service guy changed the thermostat, the heat would work for a few hours, then kicked off and wouldn't come back on. The air worked great. Now neither one will work. The thermostat clicks like it is going to but nothing at all.
The sequencer and relay are not the same?
Thanks!
Re: Nordyne FEH-105HA-04
Posted: Sun Dec 05, 2010 7:40 pm
by Robert
Sequencer controls elements and blower motor for heating.
Fan relay controls blower motor for cooling.
So now, nothing works ? No elements, no a/c and no blower for either ?
Thanks,
Robert
Re: Nordyne FEH-105HA-04
Posted: Sun Dec 05, 2010 11:41 pm
by Cindy_R
Hi.
Thats correct Robert..........no nothing works. No elements, no ac, no heat, nor the blower.
Thanks!
Re: Nordyne FEH-105HA-04
Posted: Mon Dec 06, 2010 6:41 pm
by Robert
Check transformer first for 240vac on primary-line side and 24vac on the secondary-load side.
Thanks,
Robert
Re: Nordyne FEH-105HA-04
Posted: Tue Dec 07, 2010 7:54 pm
by Cindy_R
Hi Robert:
I just wanted to thank you for all your help. I called a service guy today who came and changed all four fuses. It fixed my problem!
Now I have both heat and air again.
Thank you again for all your help.
Cindy
Re: Nordyne FEH-105HA-04
Posted: Wed Dec 08, 2010 7:49 pm
by Robert
Hi Cindy,
That's great, you're very welcome, happy to help.
Take care and best wishes,
Robert