i live in virginia furnace is in asheville nc last year thing would burn you up this year no heat.had a guy go check it,had him replace limit switch,now bottom element comes on other two:top element glows red in spots,middle element not coming on at all.i gotta assume since one element is working sequencer is sending 110v thru to elements and two are bad?how do i tell this guy troubleshooting procedures?he says no continuity thru the two elements that dont come on but i have my doubts.please help me explain it in a simple to follow way.he has a good meter
At the ends of each element coil, there will be a spade terminal/wire on a white ceramic insulator.
WITH call for heat from t-stat, wait one minute then test across those two terminals on each element coil, one meter lead on each side, for 240VAC.
IF it is there and the coil is not energizing, then disconnect one wire from one side and ohm across them with power OFF.
IF power/voltage is there and they do not work and do not show/read continuity, they are bad.
You should have 240VAC across each and 120VAC from each side terminal to a good unpainted metal ground.
Thanks,
Robert
WITH call for heat from t-stat, wait one minute then test across those two terminals on each element coil, one meter lead on each side, for 240VAC.
IF it is there and the coil is not energizing, then disconnect one wire from one side and ohm across them with power OFF.
IF power/voltage is there and they do not work and do not show/read continuity, they are bad.
You should have 240VAC across each and 120VAC from each side terminal to a good unpainted metal ground.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 2 Replies
- 60295 Views
-
Last post by jazsimpson
Sat Jul 08, 2017 8:16 am
-
- 0 Replies
- 57569 Views
-
Last post by Montanan
Wed Jan 03, 2018 1:03 pm
-
- 0 Replies
- 50110 Views
-
Last post by Kourgath
Fri Mar 23, 2018 3:41 pm
-
-
LOUD Blower on Coleman Presidential 2 900759
by AuntKatie » Thu Apr 05, 2018 6:50 pm » in Coleman Service & Repair - 0 Replies
- 44828 Views
-
Last post by AuntKatie
Thu Apr 05, 2018 6:50 pm
-
-
-
Eb12eb Coleman furnace 4 speed help.
by Johnwayne892000 » Thu Aug 30, 2018 7:37 pm » in Coleman Service & Repair - 0 Replies
- 24986 Views
-
Last post by Johnwayne892000
Thu Aug 30, 2018 7:37 pm
-