FAN WON'T SHUT OFF COLEMAN ELECTRIC EB20B

Posted: Thu Apr 28, 2011 11:26 am
by trish73
FAN KEEPS RUNNING EVEN WHEN THE THERMOSTAT IS IN THE OFF POSITION. REPLACED THE THERMOSTAT AND IT STILL RUN IN OFF. WHAT IN THE NEXT STEP?

Re: FAN WON'T SHUT OFF COLEMAN ELECTRIC EB20B

Posted: Fri Apr 29, 2011 7:52 pm
by Bill
Hi Trish,
First i would like to ask, is the heat on as well as the blower? If so then I would say it sounds like the sequencer is not working for you. Here is a link for a sequencer for your furnace.
http://www.aberdeenhomerepair.com/store ... -sequencer
If it is just the blower i would say that the fan relay is bad, here is a link for that part
http://www.aberdeenhomerepair.com/store ... -fan-relay
hope this helps you
Bill