I have a model EB15B model ac/furnace that I presume is Coleman however it doesn't say Coleman any where. The furnace is blowing only warm air. I don't see any glow from the 3 heat coils. The heat coils have a part number of 5000-218-501 and 5000-219-501. I didn't find either part number on your parts lists. Any help to why there isn't heat? Thanks.
Hi,
Yes, you have a Coleman.
Many times when heating elements don't come on, the fault is a defective sequencer. The sequencer for your furnace is part # 3115-3571. http://www.aberdeenhomerepair.com/store ... -sequencer
You can check the heating elements for resistance. Shut the power off, remove the wires and test with your meter. Use the setting on your meter that indicates continuity (the meter will beep or the needle will go all the way across if your resistance is good). Or just pull out the elements and look for any broken wires.
These are the heating elements your furnace uses: 3500-405P/A: http://www.aberdeenhomerepair.com/store ... ment-4.8KW
and 3500-410P/A http://www.aberdeenhomerepair.com/store ... ment-9.6KW
Thanks,
Mark
Yes, you have a Coleman.
Many times when heating elements don't come on, the fault is a defective sequencer. The sequencer for your furnace is part # 3115-3571. http://www.aberdeenhomerepair.com/store ... -sequencer
You can check the heating elements for resistance. Shut the power off, remove the wires and test with your meter. Use the setting on your meter that indicates continuity (the meter will beep or the needle will go all the way across if your resistance is good). Or just pull out the elements and look for any broken wires.
These are the heating elements your furnace uses: 3500-405P/A: http://www.aberdeenhomerepair.com/store ... ment-4.8KW
and 3500-410P/A http://www.aberdeenhomerepair.com/store ... ment-9.6KW
Thanks,
Mark
You can't fail if you don't try!
-
- Similar Topics
- Replies
- Views
- Last post
-
- 2 Replies
- 60293 Views
-
Last post by jazsimpson
Sat Jul 08, 2017 8:16 am
-
-
EB15B Limit switch part # help
by ferret13sj » Thu Jan 18, 2018 11:46 pm » in Coleman Service & Repair - 0 Replies
- 48084 Views
-
Last post by ferret13sj
Thu Jan 18, 2018 11:46 pm
-
-
-
Eb15b sequencer & limit switch testing
by ferret13sj » Tue Jan 25, 2022 1:56 am » in Coleman Service & Repair - 0 Replies
- 125660 Views
-
Last post by ferret13sj
Tue Jan 25, 2022 1:56 am
-