Coleman Evcon

Posted: Sat Jul 21, 2007 7:38 pm
by Guest
I got problems :roll:

I got a 1996 model Standard Blend air 11 model 7681 8191/A

well anyway I start it up the squirr cage starts rolling in the blower
and it begins to blow cool air for less time than it takes to type this and it quits
the control panel light does not blink as far as I can see I took tha panel off
can it be the air blower motor

RE: Coleman Evcon

Posted: Sat Jul 21, 2007 10:38 pm
by Robert
Hi,

To clarify, everything inside and outside starts up and runs on a/c for short time, then inside blower motor stops, but outside condenser unit keeps running ?

If so, trace blower wires back to connection point and see if the motor is getting full power.

120vac if gas furnace and 240vac if electric furnace.


Thanks,
Robert