So, Im replacing my water heater (leaky one from previous post)...And i simply pulled my T&P Relief Valve Drain pipe up out of the floor. I shined a flash light down there and all I see if belly insulation! Shouldn't this be draining to a pipe? or at least to the ground to prevent any damage to other things?
Have any of you found this while doing any water heater repairs?
T&P Relief Valve Drain Pipe
Moderators: Greg, Mark, mhrAJ333, JD
Ideally it should go through the insulation and drain onto the ground. You really don't want to fill the belly with water if it starts leaking.
Greg
Greg
"If I can't fix it, I can screw it up so bad no one else can either."
-