Posted: Fri Nov 16, 2007 1:04 pm
by Rob
coleman #7956A856.standing pilot........I put new roof on trailer and simply extended chimney.......converted from nat gas to LP....pilot stays lit....burner lites but goes out when peephole is closed....new orfice,thermocoupler,and thermostat.....would that have something to do with roof jack..chimney length ...combustion air?????...what is the fix???? Rob

RE: burner won't stay lit...chokes out

Posted: Fri Nov 16, 2007 1:07 pm
by Robert
Hi,

Did you extend it with a Coleman roof-jack extension ?


Thanks,
Robert

RE: burner won't stay lit...chokes out

Posted: Fri Nov 16, 2007 3:10 pm
by Rob
no I didn't use a coleman roof jack...but just now I noticed the data chart on the furnace..so I'll measure from the top of the furnace to the top of the roof and check the chart and order the proper roof jack from your website to start with....any other suggestions for me Robert??

RE: burner won't stay lit...chokes out

Posted: Fri Nov 16, 2007 4:08 pm
by Robert
Hi,

See what that does first. You must have the correct roof-jack and any extensions for the furnace.


You'll need the hydroment sealant to seal around the flashing and swivel joints.


Thanks,
Robert