Coleman 3400-815 not shutting off or noisy shut off

Posted: Wed Feb 20, 2008 11:18 am
by Dunsel
I have a Coleman Model 3400-815 electric furnace in my mobile home. lately when the blower shuts off, it shuts off with a rather loud noise and hesitates a little when shutting off (starts to shut off, but runs an extra second or two). One night last week it would not shut off at all. Used an ohmmeter on the thermistat and it looks to be OK. Studying the schematic attached to the unit I suspect the problem may be with the sequencer. Looking at the schematic it doesn't really look like it could be anything else but that. Does this sound correct?
I checked the sequencer and it had a 3115-357 stamped on it so it appears i need to order the 3115-3571. Does that sound correct for my make and model of furnace?
Many thanks in advance for your help and advise. I will order the part from you as soon as I get feedback to confirm that is the correct part for my unit and problem.

RE: Coleman 3400-815 not shutting off or noisy shut off

Posted: Wed Feb 20, 2008 7:45 pm
by Robert
Hi,

That is correct p/n and the most likely problem for what you stated.


Thanks,
Robert

RE: Coleman 3400-815 not shutting off or noisy shut off

Posted: Thu Feb 21, 2008 11:21 am
by Dunsel
Thanks so much for confirming that! I'll order that part today.

RE: Coleman 3400-815 not shutting off or noisy shut off

Posted: Thu Feb 21, 2008 12:02 pm
by Robert
You're very welcome, happy to help. Thanks for ordering.



Take care and best wishes,
Robert