Coleman modelDGAT056BDD

Posted: Wed Feb 10, 2010 1:23 pm
by shannon
I have a coleman furnace model#DGAT056BDD Serial #970346567 We just replaced roof jack and gas valve because the repair man said it was needed after changing the valve our blower will come on and go back off again about 6-10 times befor it will stay on and run through the cycle just fine. this was not doing this before we put the new valve in. we did this work ourselves because of the price it would cost for them to. do you have any suggestions for us to try Thank-You
Shannon

Re: Coleman modelDGAT056BDD

Posted: Thu Feb 11, 2010 3:07 pm
by Dantheswim
Not trying to steal Shannon's thunder or anything but I have the EXACT same problem except we have not replaced anything like she (or he!) has. We moved in a few months ago and it has always done the really short cycles until it eventually stays on. The burner stays lit the whole time, just the blower will do very annoying constant short cycles-- 5 or 10 seconds, then cut off...back on...off...on...off... then eventually stay on to heat the house. I have replaced the thermostat with a digital and really don't think it is the problem anyhow (also replaced the upper limit a few months ago).
I have the same model except mine is 70,000 BTU..

Re: Coleman modelDGAT056BDD

Posted: Thu Feb 11, 2010 7:08 pm
by Robert
Hi Shannon,

Inspect the burner and burner orifice behind the gas valve for blockages. Look for spider-web-eggs especially.


If ok need to have gas pressures checked by hvac tech.


Thanks,
Robert

Re: Coleman modelDGAT056BDD

Posted: Thu Feb 11, 2010 7:09 pm
by Robert
Hi Dan,

Please start a new thread with your questions/concerns.


Thanks,
Robert

Re: Coleman modelDGAT056BDD

Posted: Sun Feb 14, 2010 11:24 am
by shannon
HI Robert
I have had the pressure checked by gas company they said the pressure was really good right where it should be.They seem to be puzzled why it is doing it. They mention maybe the circut board but they said they have never seen one do this in the newer furnaces

Re: Coleman modelDGAT056BDD

Posted: Mon Feb 15, 2010 1:33 am
by Robert
Is burner and burner orifice clear ? If so, could be the control board, but would need to test the board to know.



Thanks,
Robert

Re: Coleman modelDGAT056BDD

Posted: Mon Feb 15, 2010 12:55 pm
by shannon
burner and orfice are clear. How do you test the board?

Re: Coleman modelDGAT056BDD

Posted: Mon Feb 15, 2010 8:07 pm
by Robert
Does the burner stay ignited while blower is cutting in and out ? If so, does it appear to be a normal good and strong flame ?



Thanks,
Robert

Re: Coleman modelDGAT056BDD

Posted: Wed Feb 17, 2010 8:47 pm
by clabar
i have the same furnace but mine is 56,000 btu . my light flashes ignition failure code and runs a short cycle but no heat. and the damper motor works but it buzzes all the time.any help would be a plus
model dgat056bdd
serial# 951154405

Re: Coleman modelDGAT056BDD

Posted: Wed Feb 17, 2010 9:48 pm
by Robert
Start a new thread with your questions and concerns.



Thanks,
Robert